What is it ? 23/11/2012 at 18:41 #38030
Simdmuk
Avatar
153 posts
The Robin Hood line today has suffered "a signalling problem" according to National Rail Enq. They even have a picture link to the damaged equipment. Anyone know what this equipment is ? It looks like batteries to me.

http://www.nationalrail.co.uk/service_disruptions/sa7984d1da6d4caaa4e3940d61b6a1de/details.html


http://ow.ly/i/19XQx

Log in to reply
What is it ? 23/11/2012 at 18:49 #38032
GeoffM
Avatar
6282 posts
The NX650/BX650 tells me it's a 650V supply of some sort, probably for signalling as the report suggests.
SimSig Boss
Log in to reply
The following user said thank you: Simdmuk
What is it ? 23/11/2012 at 19:22 #38034
Low Road
Avatar
1 posts
Looks like someone did not tighten up something up well enough! Just a mild case of burning.

Who forgot to torque up the connections.

Log in to reply
What is it ? 23/11/2012 at 23:43 #38038
Stephen Fulcher
Avatar
2025 posts
I have seen lightning do that to those Cammaster fuse holders as well.

BX and NX signifies an AC supply, with 650 being the voltage.

Modern UK signalling installations use 650vac single phase distribution generally, which is then transformed down to 110vac in each location, and then further still to various dc voltages as required.

Last edited: 24/11/2012 at 00:07 by Stephen Fulcher
Log in to reply
The following user said thank you: Simdmuk
What is it ? 24/11/2012 at 00:23 #38039
Firefly
Avatar
521 posts
Quote:
The NX650/BX650 tells me it's a 650V supply of some sort, probably for signalling as the report suggests.
It's the 650v supply cubical in a signalling apparatus case. The 650v supply which runs from cabinet to cabinet along the railway line will come in on one pair of links and go out on the other set (hence 4 links). The links look like this

The red switch will isolate the supply for the particular apparatus case.

The 650v runs all lineside signalling equipment so with that failure you would have lost everything.

FF

Last edited: 24/11/2012 at 10:02 by Firefly
Log in to reply
The following user said thank you: Simdmuk